. The 3000 w element will draw in excess of 13 Amps (depending on your mains supply voltage
in the uk the declared voltage is 230v so 13.05A,realistically the uk voltage sits at 240v or more, so current consumption will be closer to 12.5A,whatever current it is 1.5mm will handle that sort of current day in day out without getting excessively hot,its rated current at 60c is 16A
and use silicone insulated or some other heat resistant type of wire.
why? the temperature inside the enclosure isnt going to get much above ambient
I am not sure what the current ratings are on the crimp connectors but I would lose them if I were you.
more than enough for the job,there used all over the place,and crimps are the most common method of terminating large cables,you wont find many screw terminals that can take a 500mm
I am not sure about the regulations where you are but 2,5mm (or more ) wire is used for heating elements and plug circuits where I am.
All depends on the type of element,no need for 2.5mm if its a 15w element and 2.5mm is a bit small for an 10kw water heater, normal 13A socket are wired in 2.5mm unless it pyro then you can drop down to 1.5.if its a 16A socket 1.5mm is allowed depending on the cable length,and if its a 5A socket then 1mm is good enough