How to connect 2 sockets to one 27A cable without ring
How to connect 2 sockets to one 27A cable without ring
I'm looking at https://www.cef.co.uk/catalogue/product ... nction+box
But I'm not sure how to use it, it looks like theres 2x Neutral connections on either side, so 4 in total, would those 4 terminals
be internally connected?
But I'm not sure how to use it, it looks like theres 2x Neutral connections on either side, so 4 in total, would those 4 terminals
be internally connected?
- themadhippy
- Even further under the Table
- Posts: 2970
- Joined: Tue Dec 08, 2009 12:53 am
- Location: playing hooky
Re: How to connect 2 sockets to one 27A cable without ring
maybe,maybe not, whats wrong with the good ole circular junction box

As an aside if your intending to take a single spur from the ring to run 2 sockets the big book of electrickery rules dont like that,your only allowed 1 double or 1 single socket per unfused spur

As an aside if your intending to take a single spur from the ring to run 2 sockets the big book of electrickery rules dont like that,your only allowed 1 double or 1 single socket per unfused spur
Warning: The Dutch Coffeeshops products may contain drugs. Drinks containing caffeine should be used with care and moderation
Re: How to connect 2 sockets to one 27A cable without ring
It's just a 32 amp connector with two ins and two outs
"You're not drunk if you can lie on the floor without holding on." Dean Martin
1. Life is not a journey to the grave with the intention of arriving safely in a pretty and well-preserved body, but rather to skid in sideways, thoroughly used, totally worn out and loudly proclaiming... "f*ck, what a trip
It's better to lose time with friends than to lose friends with time (Portuguese proverb)
Be who you are
Because those that mind don't matter
And those that matter don't mind
1. Life is not a journey to the grave with the intention of arriving safely in a pretty and well-preserved body, but rather to skid in sideways, thoroughly used, totally worn out and loudly proclaiming... "f*ck, what a trip
It's better to lose time with friends than to lose friends with time (Portuguese proverb)
Be who you are
Because those that mind don't matter
And those that matter don't mind
Re: How to connect 2 sockets to one 27A cable without ring
I'd be taking a cable from the house fuse box, to the shed, and running a couple of sockets from that, with the junction box, is that ok?
Ah, so that one I linked wouldn't do the job?
With the circular type are you essentially pushing all Neutral wires for example into one of those terminals I assume?
Ah, so that one I linked wouldn't do the job?
With the circular type are you essentially pushing all Neutral wires for example into one of those terminals I assume?
- themadhippy
- Even further under the Table
- Posts: 2970
- Joined: Tue Dec 08, 2009 12:53 am
- Location: playing hooky
Re: How to connect 2 sockets to one 27A cable without ring
If its its own dedicated circuit yes fine,you need to use a 20A fuse if your using 2.5mm cable,if you want to use a 32A fuse then you need to use 4mm cablei'd be taking a cable from the house fuse box, to the shed, and running a couple of sockets from that, with the junction box, is that ok
yepWith the circular type are you essentially pushing all Neutral wires for example into one of those terminals I assume?
Warning: The Dutch Coffeeshops products may contain drugs. Drinks containing caffeine should be used with care and moderation
Re: How to connect 2 sockets to one 27A cable without ring
Awesome cheers, just going to grab one of those circle junction boxes now 

Re: How to connect 2 sockets to one 27A cable without ring
Couldn't one of your sockets also double as a junction box? That'd give you fewer connections to make. (I'm not an electrician, mind…)
Re: How to connect 2 sockets to one 27A cable without ring
Yeah don't quite understand the point of the junction box, just run a new radial circuit.
- themadhippy
- Even further under the Table
- Posts: 2970
- Joined: Tue Dec 08, 2009 12:53 am
- Location: playing hooky
Re: How to connect 2 sockets to one 27A cable without ring
maybe the layout of the sockets makes it more economical to put in a junction box and run 2 short cables instead of 2 long onesYeah don't quite understand the point of the junction box, just run a new radial circuit.
Warning: The Dutch Coffeeshops products may contain drugs. Drinks containing caffeine should be used with care and moderation
- Aleman
- It's definitely Lock In Time
- Posts: 6132
- Joined: Sun Jun 03, 2007 11:56 am
- Location: Mashing In Blackpool, Lancashire, UK
Re: How to connect 2 sockets to one 27A cable without ring
The 'Proper way to do it would be to run you cable from your house fuse box, to a smaller fuse box in the shed, and then run a ring containing your sockets in the shed from this fuse box.
You probably want 6mm cable to go from the fuse in the house to the fuse box in the shed, then run 2.5mm cable as the ring in the shed. . . . Depending on the cable run you might get away with 4mm but it depends on the resistance and voltage drop, which is a function of length. . . . If you are running exposed or buried cable then you will need armoured cable.
Then you have the issue of what to do with the earth? Do you export it from the house or add new earths??
Get some professional advice . . . and as an aside Part P prevents you personally from doing this work . . . or at least you would need to pay a fortune to the local authority to come out and certify it . . . If you have a Part P certified friend they might certify it for you, but they are then putting their reputation on your ability
You probably want 6mm cable to go from the fuse in the house to the fuse box in the shed, then run 2.5mm cable as the ring in the shed. . . . Depending on the cable run you might get away with 4mm but it depends on the resistance and voltage drop, which is a function of length. . . . If you are running exposed or buried cable then you will need armoured cable.
Then you have the issue of what to do with the earth? Do you export it from the house or add new earths??
Get some professional advice . . . and as an aside Part P prevents you personally from doing this work . . . or at least you would need to pay a fortune to the local authority to come out and certify it . . . If you have a Part P certified friend they might certify it for you, but they are then putting their reputation on your ability
Re: How to connect 2 sockets to one 27A cable without ring
I've only today read elsewhere that you're not supposed to export the earth. Apparently it should be connected at the house end and insulated from everything at the shed end, where you should have a new earth rod providing the earth for the shed because the actual earth potentials at the house and shed may be different and therefore may be unsafe in the event of an electrical failure.Aleman wrote:Then you have the issue of what to do with the earth? Do you export it from the house or add new earths??
I've also read that people often still export the earth anyhow

I'm not entirely sure I properly understand all this equipotential bonding stuff though.
James
- themadhippy
- Even further under the Table
- Posts: 2970
- Joined: Tue Dec 08, 2009 12:53 am
- Location: playing hooky
Re: How to connect 2 sockets to one 27A cable without ring
it all depends on the type of earthing arrangement on the incoming supply,if it TNC-S then no exporting the earth outside the equipotential bonding zoneI've only today read elsewhere that you're not supposed to export the earth.
Warning: The Dutch Coffeeshops products may contain drugs. Drinks containing caffeine should be used with care and moderation
- Pinto
- Falling off the Barstool
- Posts: 3443
- Joined: Sat Mar 17, 2012 4:09 pm
- Location: Rye, East Sussex
Re: How to connect 2 sockets to one 27A cable without ring
I was always under the impression there was nothing wrong with exporting the earth on TN-S or TN-CS provided you used a conductor of sufficient size connected to the incoming earth source - eg: 10mm2 - basically treat it as a main bond. The new connection just extends the EPZ to your shed ? Never seen a reg that says no...
TT of course would be a different kettle of onions
TT of course would be a different kettle of onions
Primary 1: Nonthing
Primary 2 : Nothing
Primary 3 : None
Secondary 1 : Empty
Secondary 1 : None
DJ(1) : Nowt
DJ(2) : N'otin....
In the Keg : Nada
Conditioning : Nowt
In the bottle : Cinnamonator TC, Apple Boost Cider, Apple & Strawberry Cider
Planning : AG #5 - Galaxy Pale (re-brew) / #6 - Alco-Brau (Special Brew Clone) / #7 Something belgian...
Projects : Mini-brew (12l brew length kit) nearly ready
Join the BrewChat - open minds and adults only
- Click here
Primary 2 : Nothing
Primary 3 : None
Secondary 1 : Empty
Secondary 1 : None
DJ(1) : Nowt
DJ(2) : N'otin....
In the Keg : Nada
Conditioning : Nowt
In the bottle : Cinnamonator TC, Apple Boost Cider, Apple & Strawberry Cider
Planning : AG #5 - Galaxy Pale (re-brew) / #6 - Alco-Brau (Special Brew Clone) / #7 Something belgian...
Projects : Mini-brew (12l brew length kit) nearly ready

Join the BrewChat - open minds and adults only

Re: How to connect 2 sockets to one 27A cable without ring
I think our house is TT, but I'm really not sure. I know the transformer in our field is earthed because we get paid rental for the earth cables as well as the pole and we have a local "house" earth that goes into a 100A fuse box where the power comes in that I've never seen open. For all I know there might actually be two phases delivered in there. The transformer is off an 11kV overhead supply prone to tree damage and lightning strikes, so I don't imagine they'd rely on an externally-supplied earth.
James
James
- Pinto
- Falling off the Barstool
- Posts: 3443
- Joined: Sat Mar 17, 2012 4:09 pm
- Location: Rye, East Sussex
Re: How to connect 2 sockets to one 27A cable without ring
Quick and easy check :
Is the entire supply protected by an incoming RCD switch with an earth rod outside ? TT
Does the main earth bond connect to the outer sheath of the suppliers incoming cable ? TN-S
At the incoming head (where the main fuse is) can you see the earth cable enter the head adjacent to the Neutral ? - TN-CS
Edit : Just seen that you have an overhead incomming supply - that usually signifies TT; these days it's pretty much limited to rural, non urban locations. You live in d'country ?
Is the entire supply protected by an incoming RCD switch with an earth rod outside ? TT
Does the main earth bond connect to the outer sheath of the suppliers incoming cable ? TN-S
At the incoming head (where the main fuse is) can you see the earth cable enter the head adjacent to the Neutral ? - TN-CS
Edit : Just seen that you have an overhead incomming supply - that usually signifies TT; these days it's pretty much limited to rural, non urban locations. You live in d'country ?

Primary 1: Nonthing
Primary 2 : Nothing
Primary 3 : None
Secondary 1 : Empty
Secondary 1 : None
DJ(1) : Nowt
DJ(2) : N'otin....
In the Keg : Nada
Conditioning : Nowt
In the bottle : Cinnamonator TC, Apple Boost Cider, Apple & Strawberry Cider
Planning : AG #5 - Galaxy Pale (re-brew) / #6 - Alco-Brau (Special Brew Clone) / #7 Something belgian...
Projects : Mini-brew (12l brew length kit) nearly ready
Join the BrewChat - open minds and adults only
- Click here
Primary 2 : Nothing
Primary 3 : None
Secondary 1 : Empty
Secondary 1 : None
DJ(1) : Nowt
DJ(2) : N'otin....
In the Keg : Nada
Conditioning : Nowt
In the bottle : Cinnamonator TC, Apple Boost Cider, Apple & Strawberry Cider
Planning : AG #5 - Galaxy Pale (re-brew) / #6 - Alco-Brau (Special Brew Clone) / #7 Something belgian...
Projects : Mini-brew (12l brew length kit) nearly ready

Join the BrewChat - open minds and adults only